generator feeder size

Status
Not open for further replies.

sparkyI

Member
What size feeders do I need for a 400kva 480-208volt 3 phase generator that will feed a 400 amp breaker? The engineer figured parallel run for the feeder that is approxmently 200 foot long.
 
sparkyI said:
400kva 480-208volt 3 phase generator that will feed a 400 amp breaker?

Somethings wrong here Bryan, if OP meant 480/277 that genny will produce around 1400A. You got a 400A breaker that complies with 230.95???
 
For 400KVA at 480/277, I came up with 481 amps. At 208/120, it's 1111 amps.

Quite likely, it's a 10 lead gen, meaning wye connection only. If it's connected as a series wye, the output will be 480/277, or 416/240. Depends on where the regulator is set. If it's connected as a parallel wye, it'll be 240/138, or 208/120.

A 400 amp breaker is a tad small for this gen, but there's nothing wrong with it. As far as wire size goes, it depends on whether it's copper or aluminum, single or parallel, etc. At 200', voltage drop won't be much of an issue at 480, at 208 it might be.

To give an accurate size, we need more information. In addition to the above, where is this 400 amp breaker located? Is it on the gen itself, or 200' away, at the load? Or maybe there are two breakers, one on the gen, and one at the load.

Rob.
 
generator feeder size

Sorry, wrong info. 200kva generator feeding a 400 amp 3-phase 480volt breaker after the dissconnect. I am going to run the feeders in parallel a distance of 200' between the breaker on the gen and the breaker in the panel. Like to know what size feeders should be ran.
 
2-Sets of 3/0

2-Sets of 3/0

sparkyI said:
Sorry, wrong info. 200kva generator feeding a 400 amp 3-phase 480volt breaker after the dissconnect. I am going to run the feeders in parallel a distance of 200' between the breaker on the gen and the breaker in the panel. Like to know what size feeders should be ran.
2-sets of 3/0 carrying 400A @ 480V/3-phase will give you approx. 1.36% voltage drop @ 200', but a 200kVA/0.8 PF/3-phase generator's rated output is only about 241A @ 100%. It sounds as if the generator is undersized for the load.
 
sparkyI said:
What size feeders do I need for a 400kva 480-208volt 3 phase generator that will feed a 400 amp breaker? The engineer figured parallel run for the feeder that is approxmently 200 foot long.

Forget about the breaker size at the panel, that is really not relevant.

What is the calculated load?

What size breaker is on the generator it self?
 