Hi guys, one quick question:
We have a 40kw gen-set , 3phase 120/208 volt ( not sure of PF yet) install coming up. I was curiouis if I calculate the feeders (from the Generator to the ATS) as a continuous load?
The Generator has a 150 amp main breaker, do I use the actual kw output, or base the feeder size on the 150 main breaker?
I appreciate hearing any input you may have.
We have a 40kw gen-set , 3phase 120/208 volt ( not sure of PF yet) install coming up. I was curiouis if I calculate the feeders (from the Generator to the ATS) as a continuous load?
The Generator has a 150 amp main breaker, do I use the actual kw output, or base the feeder size on the 150 main breaker?