sleepy

Senior Member
we are adding a emergency standby generator to a existing building. the building has a fire pump. we have an emergency panel, we are circuiting the firepump through this panel. so what we have is normal power and generator to transfer switch to the emergency panel that has the fire pump. been through section 695 and 700
is this good any help
thanks
 
This sounds like it is in violation of 695.3(A)1 and possibly 695.10 if the transfer switch is not rated for fire pumps, 695.12 if the transfer switch is not within sight of the fire pump and maybe 695.14 (f). This all depends on details that have not been provided.
 
generator/fire pump

rick, question 695.3(1)isn't that if you just have normal power, isn't it different if
you have a alternate source, generator, i get the other sections
thanks
 
I hope this helps


http://ecmweb.com/mag/electric_abcs_fire_pump/index1.html

Single utility service point and onsite generator
This project requires design of an onsite generator(s) sized for the fire pump's alternate power source. All the requirements of NFPA 110, ?Standard for Emergency and Standby Power System,? should be met in designing and sizing the generator system. The generator(s) must be sized to start and run the fire pump, along with any additional loads connected to it. As per NEC 695.3(B)(1), it does not need to have the capacity to handle the pump's locked rotor current. Nor does the tap for the generator feeder have to be located ahead of its disconnecting means. The generator does have to have enough fuel capacity to provide eight hours of operation at 100% of the pump's rated load (NFPA 20, 9.6.2.2). The transfer of power (from normal to standby and vice versa) needs to take place within sight of the fire pump (NFPA 20, 9.6.4 and NEC 695.12(A), which means the transfer switch needs to be located in the same room as the pump.

As with the first example, it's best to specify a packaged unit. In this case, a combination automatic transfer switch, disconnect switch, and fire pump controller is the best choice. You'll also need to route two feeders to the fire pump room. Exercise care with the routing, and be sure the cables are properly protected to ensure a successful installation, just as you did in the first example.
 