I am paralleling (3)-2MW, 277/480V generators. Due to the low zero sequence impedance, my ground fault current at the paralleling switchgear is way higher than 3-ph fault current. Per my calculation, I have
Three phase fault current: 63,483A (x?d=0.1421) (21,161amp x 3)
Ground fault current: 80,454A (x0=0.0336) (26,818amp x 3)
That being said, I have two questions.
1. Can I just provide 100K AIC CBs (instead of 65K AIC) for higher ground fault current and call it a day? Is 100k AIC CB is rated for 80k ground fault? Isn?t the 100k rating is based on the L-L rating?
2. How about adding a small reactance at the generator so that the ground fault current can be reduced to the 3-ph fault current level? Has anyone done this before? Can it be done by generator mfgrs? Or is this something that has to be done in the field?
Three phase fault current: 63,483A (x?d=0.1421) (21,161amp x 3)
Ground fault current: 80,454A (x0=0.0336) (26,818amp x 3)
That being said, I have two questions.
1. Can I just provide 100K AIC CBs (instead of 65K AIC) for higher ground fault current and call it a day? Is 100k AIC CB is rated for 80k ground fault? Isn?t the 100k rating is based on the L-L rating?
2. How about adding a small reactance at the generator so that the ground fault current can be reduced to the 3-ph fault current level? Has anyone done this before? Can it be done by generator mfgrs? Or is this something that has to be done in the field?