Generator ground rod

Status
Not open for further replies.

wdan432

New member
Do I need ground rod for air cooled Generac generator and if not what code article tells us this. Is this a seperatly derived system?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
By direct NEC Article, Dennis is correct. If the generator is a SDS, a Code required grounding electrode system is needed.
Generac Corp. in their instructions requires a ground rod, in all cases, I believe, and NEC 110.3(B) would apply.
 

wirebender

Senior Member
From a Generac installation manual.


6. Connect an approved ground strap to the grounding lug on the
base frame and to an approved earth ground or grounding rod
as specified by local regulations.
 

shortcircuit2

Senior Member
Location
South of Bawstin
From a Generac installation manual.


6. Connect an approved ground strap to the grounding lug on the
base frame and to an approved earth ground or grounding rod
as specified by local regulations.

The key wording above is "as specified by local regulations"

There are no local regulations in my area that require a ground rod and the NEC only requires a GES if it is set up as an SDS.

Installing a ground rod for a generator that is NOT set up as an SDS is supplemental.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
From a Generac installation manual.


6. Connect an approved ground strap to the grounding lug on the
base frame and to an approved earth ground or grounding rod
as specified by local regulations.

Would the building grounding eletrode system be an approved earth ground? I'm not reading this as a requirment to use a ground rod.
 