Ok this might sound like dumb question but here goes..
Why do you have to install a grounding electrode by a generator if your transfer switch connects the generator neutral to the service neutral and you also have an EGC? I feel like that's not a seperately derived system... According to 250.20(D) (Especially FPN No. 1) it's saying that it is not considered a seperately derived system if the generator neutral and service neutral are solidly connected.
Just so you don't have to look, FPN No. 1 Says "An alternate power source such as an onsite generator is not a seperately derived system if the grounded conductor is solidly interconnected to a service supplied system grounded consudctor. An example of such situations is where alternate source transfer equipment does not include a switching action in the grounded conductor and allows it to remain solidly connected to the service supplied grounded conductor when the source is operation and supplying the load served."
So here's my question. Does the switcing action of the transfer switch not count as "solidly connected" and therefore it's a seperately derived system and need supplementary grounding? Or is it saying that as long as the switch bonds the neutrals then it's not a seperately derived system and therefore doesn't need grounding? Also, wouldn't the EGC from the panel with the transfer switch to the generator be sufficient ground (EMT into that panel, and EMT from panel to gen), just as good if not better than a supplementary grounding electrode? The frame is connected to an EGC, the neutral is common with the service neutral. Why the grounding electrode?
Please help me understand, I'm rather new and I've just been taught to ALWAYS install a grounding electrode, and I realize this is a safe practice but I just want to know exactly what 250.20 means.
Thanks
Why do you have to install a grounding electrode by a generator if your transfer switch connects the generator neutral to the service neutral and you also have an EGC? I feel like that's not a seperately derived system... According to 250.20(D) (Especially FPN No. 1) it's saying that it is not considered a seperately derived system if the generator neutral and service neutral are solidly connected.
Just so you don't have to look, FPN No. 1 Says "An alternate power source such as an onsite generator is not a seperately derived system if the grounded conductor is solidly interconnected to a service supplied system grounded consudctor. An example of such situations is where alternate source transfer equipment does not include a switching action in the grounded conductor and allows it to remain solidly connected to the service supplied grounded conductor when the source is operation and supplying the load served."
So here's my question. Does the switcing action of the transfer switch not count as "solidly connected" and therefore it's a seperately derived system and need supplementary grounding? Or is it saying that as long as the switch bonds the neutrals then it's not a seperately derived system and therefore doesn't need grounding? Also, wouldn't the EGC from the panel with the transfer switch to the generator be sufficient ground (EMT into that panel, and EMT from panel to gen), just as good if not better than a supplementary grounding electrode? The frame is connected to an EGC, the neutral is common with the service neutral. Why the grounding electrode?
Please help me understand, I'm rather new and I've just been taught to ALWAYS install a grounding electrode, and I realize this is a safe practice but I just want to know exactly what 250.20 means.
Thanks