Generator Grounding

Status
Not open for further replies.

DanS26

Member
Location
IN
I have recently reviewed a homeowner site with the generator grounded as follows:

1. the main distribution panel is the first disconnect and has the neutral bonded to the ground system with a properly sized GEC connected to a properly sized grounding electrode.

2. the main grounding electrode is bonded underground to a second electrode approximately 50 feet away from the first electrode. I believe this satisfies NEC grounding requirements for a low impedance path.

3. at the second electrode site is a generator that is NOT a separate derived device (ie a floating neutral). The generator has a GEC connected to the second electrode.

My questions:

1. Does the distance of the second electrode (and the inherent resistance) create a problem in the case of a nearby lightning strike? In other words, will that resistance force high voltage into the generator as an alternative path?

2. Does the generator GEC in effect create a ground loop? (ie the loop being created by the generator EGC back to the main panel)

3. Would you recommend to disconnect the generator GEC to the second electrode?
 
.......
1. Does the distance of the second electrode (and the inherent resistance) create a problem in the case of a nearby lightning strike? In other words, will that resistance force high voltage into the generator as an alternative path?

2. Does the generator GEC in effect create a ground loop? (ie the loop being created by the generator EGC back to the main panel)

3. Would you recommend to disconnect the generator GEC to the second electrode?
I would leave things just as they are. Since the GEC at the generator is connected to the house grounding electrode system there is no issue with ground loops or lightning strikes. That is only a problem when the ground rod and conductor are isolated from the rest of the GES.
 
I see no problem with the arrangement, however IMO, it should be noted that there is still a requirement for an equipment grounding conductor to be installed with the generator conductors.
 
I see no problem with the arrangement, however IMO, it should be noted that there is still a requirement for an equipment grounding conductor to be installed with the generator conductors.

Yes, the generator has a properly installed equipment grounding conductor which is incorporated into a 4 wire connection to transfer switch and main disconnect panel all properly sized.
 