I have recently reviewed a homeowner site with the generator grounded as follows:
1. the main distribution panel is the first disconnect and has the neutral bonded to the ground system with a properly sized GEC connected to a properly sized grounding electrode.
2. the main grounding electrode is bonded underground to a second electrode approximately 50 feet away from the first electrode. I believe this satisfies NEC grounding requirements for a low impedance path.
3. at the second electrode site is a generator that is NOT a separate derived device (ie a floating neutral). The generator has a GEC connected to the second electrode.
My questions:
1. Does the distance of the second electrode (and the inherent resistance) create a problem in the case of a nearby lightning strike? In other words, will that resistance force high voltage into the generator as an alternative path?
2. Does the generator GEC in effect create a ground loop? (ie the loop being created by the generator EGC back to the main panel)
3. Would you recommend to disconnect the generator GEC to the second electrode?
1. the main distribution panel is the first disconnect and has the neutral bonded to the ground system with a properly sized GEC connected to a properly sized grounding electrode.
2. the main grounding electrode is bonded underground to a second electrode approximately 50 feet away from the first electrode. I believe this satisfies NEC grounding requirements for a low impedance path.
3. at the second electrode site is a generator that is NOT a separate derived device (ie a floating neutral). The generator has a GEC connected to the second electrode.
My questions:
1. Does the distance of the second electrode (and the inherent resistance) create a problem in the case of a nearby lightning strike? In other words, will that resistance force high voltage into the generator as an alternative path?
2. Does the generator GEC in effect create a ground loop? (ie the loop being created by the generator EGC back to the main panel)
3. Would you recommend to disconnect the generator GEC to the second electrode?