I had a question about generator grounding. Typically, when we install generators we use a 4 pole ATS that switches the neutral so the generator is considered a separately derived. In this system the ground and neutral are bonded together at the generator and the generator has its own ground rod.
The job I am working on now is a little different because the ATS is only a 3 pole so it does not switch the neutral. As a result the generator is considered a non separately derived system. In this system the bonding jumper between the neutral and the ground is removed and according to 250.35(B) a bonding jumper needs to be installed between the generator equipment grounding terminal and the equipment grounding terminal in the generator control panel (disconnecting means). And no ground rod is needed. Is this correct?
The job I am working on now is a little different because the ATS is only a 3 pole so it does not switch the neutral. As a result the generator is considered a non separately derived system. In this system the bonding jumper between the neutral and the ground is removed and according to 250.35(B) a bonding jumper needs to be installed between the generator equipment grounding terminal and the equipment grounding terminal in the generator control panel (disconnecting means). And no ground rod is needed. Is this correct?