We are installing a 3P 120/208 Gen Set with Over current Protection – We have Building A and B on the same premises – the Gen is located in Building B we have a set of feeders in PVC feeding a 200A 3 Pole ATS (Non Separately Derived System) in bulding A What is the recommended Grounding Between the 2 buildings for the Emergency Back Up without bonding the two grounding systems – Building A and B have separate services
equipment grounding condcutors run with the feeder circuit conductors to the separate structure and connected at the equipment there
equipment grounding condcutors run with the feeder circuit conductors to the separate structure and connected at the equipment there