I have a customer that has two generators 480/277 VAC 3 phase 4 wire that are the stand by power for a site. Both Generators have a main circuit breaker at the generator. The generators are outdoors in separate enclosures and the main service and ATS?s for this site are located 50 feet away in the building.
Generator One feeds the Normal of ATS One, Generator Two feeds the Emergency of ATS One, The Load of ATS One feeds the Emergency of ATS Two, the Normal of ATS Two is utility and the load of ATS Two is the site load.
The ATS are 4 poles, and the Main (normal utility) service is grounded per the NEC. Neither generator neutral is grounded, when connected to either generator the site is operating un-grounded.
The customer feels the generators neutrals should be bonded to the ground in the ATS?s. I feel the generator neutrals should be grounded at the generator; I referenced 250.30 (A) (1).
Any thoughts?