I disagree; I ask just why we are driving the rod in the first place. If we are driving the rod as an electrode then this electrode must meet the requirements for an electrode.
If we are driving the electrode to keep the genset tied down so the wind don?t blow it away then it up to our own discretion.
There is this concept that there is an electrode at the service. In the event that feeders were supplying a remote building one could argue that the electrode system is already installed at the service so why install another at the remote building. The same holds true for the genset which is the same thing as the remote building.
In the 2011 code cycle there was language added to state that in no case could an EGC be used to connect any grounding electrode.
250.121 Use of Equipment Grounding Conductors.
An equipment grounding conductor shall not be used as a grounding electrode conductor
5-259 Log #4526 NEC-P05
Final Action: Accept
(250.108 (New) )
_______________________________________________________________
Submitter: Phil Simmons, Simmons Electrical Services
Recommendation: Create a new Section 250.108 as follows:
250.108 Use of Equipment Grounding Conductors.
An equipment grounding conductor shall not be used as a grounding electrode conductor.
Substantiation: This new section will clarify that grounding electrode conductors and equipment grounding conductors serve a different purpose in the electrical safety system, are sized differently and have different installation requirements. Equipment grounding conductors do not normally carry current while a grounding electrode conductor may normally carry current since it is often in parallel with the neutral conductor.
Panel Meeting Action: Accept
Panel Statement: The panel notes that this new section is to be located in Part VI and suggests it be numbered as Section 250.121.
Number Eligible to Vote: 16
Ballot Results: Affirmative: 16
So to say that the equipment grounding conductor between the genset and the service connects to the electrode system for the service just don?t fulfill the requirements of the NEC.