A have a residence that has a 200 amp main distribution panel. There is no POCO service. The 200 amp panel has two interlocked breakers connected to generators. Breaker #1 connects to a 20 kw permanently installed generator with a 4 wire 240/120 + G connection (the neutral is not bonded at the generator).
Generator #2 is a cord and plug connected portable with 240/120 3 wire cable.
My opinion is that the MDP must have a neutral-ground bond.
Any one see a problem with this installation ?
Generator #2 is a cord and plug connected portable with 240/120 3 wire cable.
My opinion is that the MDP must have a neutral-ground bond.
Any one see a problem with this installation ?