Customer wants a Generator inlet 30 amp. home has a meter main disconnect outside. Inside the home there is a 200 amp main lug panel. how would i go about installing the circuit?
If there is no provision for the inlet breaker to go in the meter main with a listed interlock then you might need to install a main breaker in the panel along with the interlock.Customer wants a Generator inlet 30 amp. home has a meter main disconnect outside. Inside the home there is a 200 amp main lug panel. how would i go about installing the circuit?
I have same issue. But I installed a 200amp panel inside with a 200 amp main. I was going to add Interlock kit on the 200amp main which would be a sub panel technically because my main disco is outside. Hopefully I pass I don’t see why I wouldn’t if utility power is isolatedCustomer wants a Generator inlet 30 amp. home has a meter main disconnect outside. Inside the home there is a 200 amp main lug panel. how would i go about installing the circuit?
Ok so this is code complaint I’m doing a service upgrade 100-200 will have outdoor meter main 200amp disconnect inside I’m adding a 200 amp sub panel but the sub panel will have a 200amp main breaker in it. I was going to install an interlock on the main and the generator breaker so it isolates from utility. I just have never used one on a sub panel before.I have replaced the MLO loadcenter inside with a MB guts, then use an interlock kit.
As long as the generator power is prevented from backfeeding the grid, it doesn't matter where the interlock is placed in the main disconnect or subpanel.Ok so this is code complaint I’m doing a service upgrade 100-200 will have outdoor meter main 200amp disconnect inside I’m adding a 200 amp sub panel but the sub panel will have a 200amp main breaker in it. I was going to install an interlock on the main and the generator breaker so it isolates from utility. I just have never used one on a sub panel before.
Thank you!As long as the generator power is prevented from backfeeding the grid, it doesn't matter where the interlock is placed in the main disconnect or subpanel.