Recently there has been an increase of home backup power/ generator supply in our area.Most often these are being installed as a entire or whole house supply.Commonly 20 kw with a service rated disc or equivalent.
With that being understood ,Now ,We are required to test run and set up the run time weekly or etc..Our inspection dept. does verify the voltage output.We are having issues with a small amount of voltage being present with the Xfer being in the open position during the generator run cycle back feeding onto the incoming supply. We have had as much as 10 v. and as low as 1.5v.
Our concern is ,with all the ( as an example residents gen sets) in a neighborhood having similar voltage back feed multiplied is the linemans safety .Thank you..