Scenario #1 :
I ordered a 55 KW, 3 phase generator several months ago through a dealership (actually an electrical supply house). The generator is being installed at a summer day camp facility and is being used to supply emergency power for (4) 3 phase pool motors only. The utility power feeding the existing breaker panel is currently a 3-pole, 100 amp breaker and has never tripped on overload. The salesman who designed and spec'd the generator decided to propose a 55KW unit. There was never any mention of the size wire to be run to the unit. The utility wiring feeding the breaker panel is # 2, copper, THHN. I chose to bump the feeders to the generator up to #1, copper, THHN based on NEC 445.13 and table 310.16 (rated at 150 amps - 90 degree column). The unit came shipped in with a 200 amp main breaker. ( The wires feeding the main breaker from the generator are paralled # 6's)
Question : Am I in violation with the wire size between the generator and disconnect switch ?
Scenario # 2 :
I ordered a 17KW portable generator that came with a 16 circuit, Siemens' main lug emergency panel for the same facility but for the 1st floor of the office building. The panel, itself (as per the label on the cover), is rated at 125 amps. There are two breakers (2-P 50 amp on standby and 2-P 60 amp on utility) installed at the top and are interconnected so that neither breaker can be on while the other is on. However, because Siemens decided to install the 50 amp breaker as the standby and the 60 amp breaker as the utility service they've placed a label on the cover stating that the panel is only rated for 60 amps.
Question #2 : (Assuming the label is there for standby electrical service only) If I replace the 2-P 60 amp breaker with a 2-p 100 amp serving as the utility feed into the main lug panel and then another 100 amp to serve an existing lighting load only panel on the load side, will I be in violation ? Bear in mind, this panel will NEVER come anywhere near maximum load either under utility or standby power.
Thanks in advance:smile: . Any comments (pro or con) will be appreciated
I ordered a 55 KW, 3 phase generator several months ago through a dealership (actually an electrical supply house). The generator is being installed at a summer day camp facility and is being used to supply emergency power for (4) 3 phase pool motors only. The utility power feeding the existing breaker panel is currently a 3-pole, 100 amp breaker and has never tripped on overload. The salesman who designed and spec'd the generator decided to propose a 55KW unit. There was never any mention of the size wire to be run to the unit. The utility wiring feeding the breaker panel is # 2, copper, THHN. I chose to bump the feeders to the generator up to #1, copper, THHN based on NEC 445.13 and table 310.16 (rated at 150 amps - 90 degree column). The unit came shipped in with a 200 amp main breaker. ( The wires feeding the main breaker from the generator are paralled # 6's)
Question : Am I in violation with the wire size between the generator and disconnect switch ?
Scenario # 2 :
I ordered a 17KW portable generator that came with a 16 circuit, Siemens' main lug emergency panel for the same facility but for the 1st floor of the office building. The panel, itself (as per the label on the cover), is rated at 125 amps. There are two breakers (2-P 50 amp on standby and 2-P 60 amp on utility) installed at the top and are interconnected so that neither breaker can be on while the other is on. However, because Siemens decided to install the 50 amp breaker as the standby and the 60 amp breaker as the utility service they've placed a label on the cover stating that the panel is only rated for 60 amps.
Question #2 : (Assuming the label is there for standby electrical service only) If I replace the 2-P 60 amp breaker with a 2-p 100 amp serving as the utility feed into the main lug panel and then another 100 amp to serve an existing lighting load only panel on the load side, will I be in violation ? Bear in mind, this panel will NEVER come anywhere near maximum load either under utility or standby power.
Thanks in advance:smile: . Any comments (pro or con) will be appreciated