Generator interlock kits

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
They're great IMO.

They have been discussed a number of times here.

SQ D and Seimens make their own versions

Roger
 

electricmanscott

Senior Member
Location
Boston, MA
They are great. I've used a bunch of them.

The Siemens/Murray version are even better. They just snap on. But for a retrofit application the interlock kit is the way to go.

I'd use them in my own house but it's way easier to backfeed a dryer receptacle. ;)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I think they are a lawsuit waiting to happen.

I'm like John, can you explain your reason please.

If your worried about someone deliberatly defeating the designed operation of the product, it would be the same as defeating any products design.

Of course, there is always the double ended male dryer cord, AKA widow maker. :D


Roger
 

JohnME

Senior Member
Also, would you guys feel comfortable using a 10/3 romex to feed the outside power inlet box? My only concern is having the customer try to run all kinds of loads and the 10/3 will not be sized correctly. I suppose if I use a 30a breaker it would eliminate this overload concern anyway.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
While they are functional and meet the intent of the code, are they listed as "transfer equipment", or does the combination of breakers and the interlock kit become "transfer equipment" when you assemble the pieces. 702.4, 702.6
 

electricmanscott

Senior Member
Location
Boston, MA
Also, would you guys feel comfortable using a 10/3 romex to feed the outside power inlet box? My only concern is having the customer try to run all kinds of loads and the 10/3 will not be sized correctly. I suppose if I use a 30a breaker it would eliminate this overload concern anyway.

What size generator are you talking about?
 

JohnME

Senior Member
The customer doesnt have one yet, they plan to have the install done and then before the winter months will purchase one.

I sized up their needs to be around 4000w, and recommended a 6-7000w unit for a buffer since they have a well pump and a furnace which would potentially draw a fair amount at startup.
 

Rewire

Senior Member
I'm like John, can you explain your reason please.

If your worried about someone deliberatly defeating the designed operation of the product, it would be the same as defeating any products design.

Of course, there is always the double ended male dryer cord, AKA widow maker. :D


Roger

Removing the panel cover defeats the interlock,I see this as a design flaw that could be the basis for a wrongful death suit. Everyone knows coffee is served hot but look what it cost Mc Ds.People will use these devices until someone gets killed an a large settlement is awarded I just don't want to be the "one".

I think a fix to this would be to design the lock to cover a panel screw while in generator mode so the panel could not be removed
 

480sparky

Senior Member
Location
Iowegia
Removing the panel cover defeats the interlock,I see this as a design flaw that could be the basis for a wrongful death suit. Everyone knows coffee is served hot but look what it cost Mc Ds.People will use these devices until someone gets killed an a large settlement is awarded I just don't want to be the "one".

I think a fix to this would be to design the lock to cover a panel screw while in generator mode so the panel could not be removed

And McDonald's not only still serves hot coffee, but hot chocolate as well now.

Tamper-resistant screws would be a good option when installing one of these critters.
 

JohnME

Senior Member
The panel cover shouldnt be off while energized anyway, theres your defense. If they take the cover off, its on them.
 

Rewire

Senior Member
The panel cover shouldnt be off while energized anyway, theres your defense. If they take the cover off, its on them.

A second year law student could rip that to shreads,coffee is hot and should not be held in the lap while driving...Mc Donalds still payed and they had a team of lawyers.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Removing the panel cover defeats the interlock,

And tyeing a lawn mowers safety handle down would defeat it's purpose.

Defeating a safety device can be done to anything, a live panel is supposed to have it's cover on, if someone removed the cover the interlock device is not in place.

Lawsuits are going to happen period.

Roger
 