Generator Interlock

Merry Christmas

Anthony1971

Member
Location
Massachusetts
Occupation
Electrician
Hi my name is Anthony I am an Electrician in Massachusetts .I am mostly An Industrial Electrician so I’m not familiar with the residential codes . I’m upgrading my service to 200 amp and I have a question about the generator interlock. I know by putting the meter main outside is your first point of disconnect and your neutrals and grounds are bonded in there then they are seperated in the inside panel which is now the subpanel My question is I have a main breaker in the sub panel and I like to put it in there and should the neutral be bonded in the genarator because they are seprtate in the sub panel it’s a portable generator. .
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Are you using a breaker interlock for switching ?
If you are not switching the neutral from the generator it is not a SDS and the neutral must not be bonded at the generator.
 

Anthony1971

Member
Location
Massachusetts
Occupation
Electrician
Yes I was going to put a interlock switch to interlock the 2pole 30amp breaker with the 200 amp breaker in the sub panel after the meter main where the the grounds and neutrals are separated
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes I was going to put a interlock switch to interlock the 2pole 30amp breaker with the 200 amp breaker in the sub panel after the meter main where the the grounds and neutrals are separated
So you will need an inlet, 2 pole 30, interlock kit and signs. Don't forget to check Article 702 for the required signage.
 

Anthony1971

Member
Location
Massachusetts
Occupation
Electrician
So you will have a meter---Transfer Switch with Main that feeds a main breaker sub panel. From the sub you will have a 4 wire inlet so your neutrals and grounds are separated.

View attachment 2571713
Here’s the interlock I got for the sub panel to lock out the 200amp breaker and 30 amp breaker
 

Attachments

  • IMG_3333.png
    IMG_3333.png
    402.8 KB · Views: 6
  • IMG_3335.png
    IMG_3335.png
    591.9 KB · Views: 6

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
So you will have a meter---Transfer Switch with Main that feeds a main breaker sub panel. From the sub you will have a 4 wire inlet so your neutrals and grounds are separated.

View attachment 2571713


Sorry I didn't mean Transfer Switch but rather a meter / main panel to the sub. I think you have the right idea. The interlock must be designed for whatever panel you have at the house. geninterlock.com has all the different interlocks for many different panels.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Is there a specific height for the generator inlet box
No code required height but I put mine high enough that I would be able to see how to line it up to plug it in.
Usually if your power is out the weather sucks too and you want to be able to plug it in quickly.
 