This is a new service at a wholesale box store. Outdoor service equipment is
sec 1. Utility tie in
sec 2. 3000a 4pole kirk key main breaker
sec 3. Is bussed to both main c.b and gen c.b. load side, also has lugs for MDP inside bld.
sec 4. 1600a 4pole kirk key c.b., fed from a gen tap box with-in 10 feet
gen tap box- provides termination for A,B,C,N, and GRD. This leads me to believe that the
gen will have the N/G bonded. (note) the gen is not on site, it is the type mounted in a
trailer pulled by a semi truck.
Ok, the Sq'D' equipment has MBJ ( neutral disconnect link ) on the line side of both the
breakers, plus if the gen has N/G bonded we have a violation, regrounding the neutral.
Before I talk to sq'd' I thought I would like to hear comments from the Forum. THX