Nxtu said:I have an AC Generator Rated 400 KW /230 V /60HZ /3Ph .If I change its voltage configuration from 220V to 460 V.
Is this change effect the KW and How it can be Calculated ....?
Thanks
Are you assuming about a 0.8 pf?jrannis said:KW will stay the same, your output amperage will be reduced from 1200 amps to 600amps.
Or a service factor maybe?Besoeker said:Are you assuming about a 0.8 pf?
jrannis said:Reading it off of my handi dandi cheat card
Nxtu said:I have an AC Generator Rated 400 KW /230 V /60HZ /3Ph .If I change its voltage configuration from 220V to 460 V.
Is this change effect the KW and How it can be Calculated ....?
Thanks
Strictly that gives W, not kW.fjrivera said:In theory, real power KW it is not affected by changing the generator output voltage. The following equation is used to calculate Real power KW as follows:
Real Power KW=sqrt(3)*Voltage*Current*Power Factor
Thanks for that and for helpfully including the page number.jrannis said: