Generator Load Calculation

HuntNJ

Member
Location
NJ
Occupation
Electrician
I have a customer who wants a generator. The inspector is asking for a load calculation. I have never done one before and when i google search i do not get any results that help me. l used to use kohlers load calculator but it seems they have taken it away from their site. Any input is appreciated. Thank you!
 

HuntNJ

Member
Location
NJ
Occupation
Electrician
whole house generator with ATS. Electrical appliances are stove refrigerator, mini split ac and dryer. i will load shed dryer and stove and its a 1600 sq ft house
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
whole house generator with ATS. Electrical appliances are stove refrigerator, mini split ac and dryer. i will load shed dryer and stove and its a 1600 sq ft house
Do the calculations as you would if it's a new service, minus the shed loads. That will give more than adequate size of generator. I suspect what you are shedding will not be worth the effort. Your transfer switch will need to be rated for the typical NEC service calculation for the dwelling. Check your copy of the NEC.
 