Yes, you’ll need to do a load calc. I often use the optional method for simplicity when sizing for generators.
If you’re looking at a new Generac 22KW, the transfer switch has built in load shedding capability for 4x HVAC units, and you can buy more wireless load shed modules; you may already be aware of this idk. I’ve got four 22kw units on order now for houses that have 400A services, so it’s not uncommon. These customers only wanted to run one or two of their HVAC units and all of the lighting/receps. They all have gas appliances. If the customer tells me they want to run everything with no load shedding, I can usually get by with a 36kw on 200A services and a 45kw on 400A services. Some need more, some need less.
Just FYI, generac just released a 24kw air cooled unit.