I Have A 180kw Gen. @ 208 3ph.
When I Calculate Load Capacity I Apply P.f. Of 0.8 To The Calculation.
The Plan Reviewer Apparently Did Not.
Isn't This The Way Is Typically Done?
My Load = 625 Amps ( 180kw/360/0.8 )
His Load = 500 Amps ( 180kw/360 )
Who Is Right?
Thanks For Input
(Edited to correct the display, in that the "0.8 pf" was not visible in the display.)
When I Calculate Load Capacity I Apply P.f. Of 0.8 To The Calculation.
The Plan Reviewer Apparently Did Not.
Isn't This The Way Is Typically Done?
My Load = 625 Amps ( 180kw/360/0.8 )
His Load = 500 Amps ( 180kw/360 )
Who Is Right?
Thanks For Input
(Edited to correct the display, in that the "0.8 pf" was not visible in the display.)