When calculating the load for an optional standby generator how do you figure motor loads. I seem to recall something about locked rotor amps but can't find it now.:-?
roger said:Are you calculating the loads served for an ATS or sizing the Generator?
Roger
Thanks, Bryan.bphgravity said:Don't worry about the LRC of motors when sizing optional standby systems. Just use one of the methods outlined in Article 220. Motors are covered in 220.50, which refers you back to Article 430.
When all is said and done, you simply need to add 25% to FLC of the motor load.
kingpb said:CAT makes a simple program (downloadable off internet) that works for simple installations, and it easy to use.
kingpb said:I will find it and post a link.
kingpb said:It seems you may now have to contact the local dealer and then they will send you a disk, but it is free.