we have a 28kw 480/277 generator for primarily emergency lighting, it has a 100 amp 3 pole brkr, broadcrown is manufacturer. neutral is switched
ats is asco 100 amp, 2 lighting loads 1 auto switched and 1 manually switched in another bldg.
what is the total load i can put on this 28 kw generator?
28 X 1000 = 28000 / 830 = 33a per phase @ 480vac
28 x 1000 = 28000 / 360 = 77a per phase @ 208vac
i want to feed approx 1600 sq ft area with power and lighting circuits, i am calculating feeding a 10 to 15 kva xfmr 208 3 ph for this additional load.
do i have enough power to do this?
thanks
ats is asco 100 amp, 2 lighting loads 1 auto switched and 1 manually switched in another bldg.
what is the total load i can put on this 28 kw generator?
28 X 1000 = 28000 / 830 = 33a per phase @ 480vac
28 x 1000 = 28000 / 360 = 77a per phase @ 208vac
i want to feed approx 1600 sq ft area with power and lighting circuits, i am calculating feeding a 10 to 15 kva xfmr 208 3 ph for this additional load.
do i have enough power to do this?
thanks