I'm planning a generator installation where the customer would like to have the capability to feed various existing distribution panels during a power outage from one portable generator.
My thought was to set up a 600 amp, 480 volt, 3R generator panel board on an outside wall fed by a 600 amp arc-tite receptacle which the 500 KVA portable generator will plug into and then have distribution from the generator panel board to the various distribution panels. Each 100 amp circuit off of the main generator panel would go to a transfer switch which would be tied into the existing 200 amp distribution panel. The customers intent is to control their loads during an outage manually.
Two questions that come to mind are: Do I need a main on the generator panel board? Do I need a disconnecting means/ OCP between the existing distribution panels and the transfer switches? I thought yes to the first question and no to the second.
BTW, the reason we're proposing to install a 600 amp system is for planned future expansion.
Any input is greatly appreciated.