shockking
Member
- Location
- Sacramento, CA
- Occupation
- engineer
Trying to settle an age old debate in the office... What is wrong with these arrangements? What code section is violated? What risk is introduced?
![1669749933262.png 1669749933262.png](https://forums.mikeholt.com/data/attachments/26/26687-727d15c41f88872849da3d63ea229e49.jpg)
![1669749978321.png 1669749978321.png](https://forums.mikeholt.com/data/attachments/26/26688-7d2fe462ca1095bff7c802bf405f4ce0.jpg)
Base case is the un-modified figure from Mike Holts, showing a generator and transfer switch with solidly bonded neutral.
Case 1 shows adding a ground rod at the transformer. Ground rod is only connected to the generator ground (not the neutral). The neutral is only bound to ground at the service panel.
Case 2 shows case 1 with the addition of a bonding jumper from generator neutral to new ground rod. There are two neutral-to-ground connections.
![1669749933262.png 1669749933262.png](https://forums.mikeholt.com/data/attachments/26/26687-727d15c41f88872849da3d63ea229e49.jpg)
![1669749978321.png 1669749978321.png](https://forums.mikeholt.com/data/attachments/26/26688-7d2fe462ca1095bff7c802bf405f4ce0.jpg)
Base case is the un-modified figure from Mike Holts, showing a generator and transfer switch with solidly bonded neutral.
Case 1 shows adding a ground rod at the transformer. Ground rod is only connected to the generator ground (not the neutral). The neutral is only bound to ground at the service panel.
Case 2 shows case 1 with the addition of a bonding jumper from generator neutral to new ground rod. There are two neutral-to-ground connections.