Since previous thread was about the customer owned transformer and neutral to ground bond in the fire pump controller/ATS, I created new thread about generator neutral to ground bond question so its not confusing.
I have fire pump controller/ATS with 3 poles that has neutral to ground bond. The fire pump controller/ATS feeds only the 3 phase fire pump. One side is fed from customer owned transformer and the backup side is feed from emergency generator that supplies only the three phase fire pump.
The generator is outdoor 240 feet away from fire pump room where fire pump controller/ATS is. Generator brings 3 phase conductors and one ground to the fire pump controller/ATS.
Should the generator have neutral to ground bond as shown in the attachment or not?