Sorry to bring up this subject again. I surveyed the past topics and rapidly became brain dead. I'm not the sharpest tack in the box.
I have a CNG facility which gets its power from the Utility, though a transformer down to a 480V switchboard and on out. I have brought the neutral from the transformer to the main breaker section, bonded it to the ground bus and to the GEC. There are no neutral loads in the plant.
This facility wants to bring in portable generator, when the main service is down, to power up about half of the load. This is to be done through another breaker, key-interlocked with the main breaker. There is no transfer switch. This might be what the NEC calls an "Optional Stand-By System" Art. 702. Not sure about that.
My question is what to do about the generator neutral? I'm thinking I need to bring it in and attach it to the same place my main feeder neutral is connected - mimicking the same connection as the main service.
I just don't know if this is correct. What do you guys think? Thanks.
I have a CNG facility which gets its power from the Utility, though a transformer down to a 480V switchboard and on out. I have brought the neutral from the transformer to the main breaker section, bonded it to the ground bus and to the GEC. There are no neutral loads in the plant.
This facility wants to bring in portable generator, when the main service is down, to power up about half of the load. This is to be done through another breaker, key-interlocked with the main breaker. There is no transfer switch. This might be what the NEC calls an "Optional Stand-By System" Art. 702. Not sure about that.
My question is what to do about the generator neutral? I'm thinking I need to bring it in and attach it to the same place my main feeder neutral is connected - mimicking the same connection as the main service.
I just don't know if this is correct. What do you guys think? Thanks.