So I am far from home, kind of on vacation, helping a friend install a generator. I decided i would not bring my codebook because I thought things would be straightforward, but sure enough murphy came along and the generator is set up a bit differently than the ones I usually do. The location is a residence, 100A automatic 2- pole transfers swtich (thus not a sds). Generator is 17 kw kohler. Every generator I have done has a breaker on the generator, so I simply size the wire to that breaker. However the manual of this unit implies that it just has a terminak block (I dont have the unit yet but need to get the groundwork done due to limited time). If this is the case:
1. Do I need to install a dsco at the generator? From memory I think there is a "if within sight" qualifier but i dont recall if that is for a disco at the generator or where the feeder connects to the premises.
2. How is the generator feeder sized/protected. Do I need an ocpd or since the generator is current limited do I size the wire to the generator max current plus a safety factor like with a pv system?
Thanks, I much appreciate any input.
1. Do I need to install a dsco at the generator? From memory I think there is a "if within sight" qualifier but i dont recall if that is for a disco at the generator or where the feeder connects to the premises.
2. How is the generator feeder sized/protected. Do I need an ocpd or since the generator is current limited do I size the wire to the generator max current plus a safety factor like with a pv system?