Generator OCPD

Status
Not open for further replies.

m sleem

Top-notch Сasual Dating - Real-life Females
Location
Usa
Occupation
Health
Can generator connects directly to ATS without OCPD?
 
Can generator connects directly to ATS without OCPD?

We hat are you trying to protect? The genset or cable? iOS the genset even capable of tripping an OCPD?
Also, I am assuming that you are referring to am ASCO contactor type ATS. There is also the breaker type ATS as available from Eaton.
 
A disconnect is not needed for that reason but I do believe OCP is required to protect the ATS.
Sorry when I said disconnect I meant with overcurrent protective device since hat was what the op asked... Thanks for clarifying tho
 