Hello everyone:
The client is planning on installing 1000KW, 480Y/277V, natural gas, standby generator that will be backing up a 1200A building main service switchboard via 1200A ATS. The feeder between the generator and the switchboard is (3) sets of 600KCmil which has 1260A ampacity). I assume the generator output breaker will be set around 1503A. Now my questions:
1. Can we still use the (3) sets of 600Kcmil since the main switchboard is protected by 1200A main breaker or we need to dial down the generator output breaker to 1200A?
2. If we dial down the generator output to 1200A, this will limit the generator output to 800KW. Will this has impact on the generator performance beside limiting the capacity?
I don't see an issue with the feeder sizes since it's protected by 1200A breaker at the main service but I think we will have an issue with the ATS since it's rated at 1200A and we don't have an option but to dial down the generator breaker to 1200A.
Any thoughts?
Thanks,
The client is planning on installing 1000KW, 480Y/277V, natural gas, standby generator that will be backing up a 1200A building main service switchboard via 1200A ATS. The feeder between the generator and the switchboard is (3) sets of 600KCmil which has 1260A ampacity). I assume the generator output breaker will be set around 1503A. Now my questions:
1. Can we still use the (3) sets of 600Kcmil since the main switchboard is protected by 1200A main breaker or we need to dial down the generator output breaker to 1200A?
2. If we dial down the generator output to 1200A, this will limit the generator output to 800KW. Will this has impact on the generator performance beside limiting the capacity?
I don't see an issue with the feeder sizes since it's protected by 1200A breaker at the main service but I think we will have an issue with the ATS since it's rated at 1200A and we don't have an option but to dial down the generator breaker to 1200A.
Any thoughts?
Thanks,