I would advise caution in the use of language here. If you are providing back-up power for a data center, and if the reason you are doing this is related to business and profit and serving your customers, then the word ?emergency? does not apply. In the context of electrical codes, that word is related to the protection of life and limb. It may be appropriate to run an ailing generator to the point of its own destruction, if that action helps people get out of an unsafe building. It is not appropriate to allow a generator to self destruct, if that action is only done to protect information.
Your installation would fall under 702, ?Optional Standby Systems,? and not under 700, ?Emergency Systems,? or 701, ?Legally Required Standby Systems.? But that is as far as I can take an answer. I do not know where in the code you can find a statement that permits the disabling of a safety shutdown feature.