bdarnell
- Indianapolis, IN
- Retired Engineer
Article 445.13 states:
The ampacity of the conductors from the generator terminals to the first distribution device(s) containing overcurrent protection shall not be less than 115 percent of the nameplate current rating of the generator. It shall be permitted to size the neutral conductors in accordance with 220.22. Conductors that must carry ground-fault currents shall not be smaller than required by 250.24(B). Neutral conductors of dc generators that must carry ground-fault currents shall not be smaller than the minimum required size of the largest conductor.
Exception: Where the design and operation of the generator prevent overloading, the ampacity of the conductors shall not be less than 100 percent of the nameplate current rating of the generator.
My question is, if a generator has an output breaker at the generator, does the exception apply here ? I think it does, but I'd like the Forum opinion.
Thanks
Thanks