I am having a generator and transfer switch installed in my home and have a question. 240/120 Single Phase.
I understand that Neutral and Ground are only to be bonded together at the main panel. I am all conduit here, and "ground" is tied to the conduit via the main panel chassis. The generator does not bond neutral and ground, it is Non-SDS.
In the "subpanel" that will be connected to the transfer switch there will be 2 hots and a neutral coming from the Transfer switch. Would it be correct to remove the bond between the left and right neutral bars. Tie all my load neutrals to the bar with the neutral running back to the transfer switch. Bond the "ground" bar ONLY to the subpanel with the bonding screw, and connect the ground bar back to the main panel ground.
That is what I am understanding as correct...or is the conduit "network" connection between the main panel and subpanel enough to cover the ground requirement?
[ July 31, 2005, 10:38 PM: Message edited by: aejanis ]
I understand that Neutral and Ground are only to be bonded together at the main panel. I am all conduit here, and "ground" is tied to the conduit via the main panel chassis. The generator does not bond neutral and ground, it is Non-SDS.
In the "subpanel" that will be connected to the transfer switch there will be 2 hots and a neutral coming from the Transfer switch. Would it be correct to remove the bond between the left and right neutral bars. Tie all my load neutrals to the bar with the neutral running back to the transfer switch. Bond the "ground" bar ONLY to the subpanel with the bonding screw, and connect the ground bar back to the main panel ground.
That is what I am understanding as correct...or is the conduit "network" connection between the main panel and subpanel enough to cover the ground requirement?