SceneryDriver
Senior Member
- Location
- NJ
- Occupation
- Electrical and Automation Designer
In the 2017 NEC, 445.18 (B) states that a prime mover for a generator greater than 15KW needs a shutdown provision "external to the equipment room or generator enclosure..."
Does this requirement extend to a 20KW natural gas-fired standby generator for a residence? I'm being asked if a shutdown provision is needed for a generator I recently installed. I can probably provide one, but there's no factory provision for the connection, and it will probably void the Millbank warranty if I go splicing into the genny's control wiring to install an E-stop pushbutton.
For reference, I can yank the 20A 12V fuse that's part of the control circuit, and that will prevent the genny from starting, but that's "inside the generator enclosure," so I'm not sure it qualifies as a shutdown means.
Thoughts?
Thanks,
SceneryDriver
Does this requirement extend to a 20KW natural gas-fired standby generator for a residence? I'm being asked if a shutdown provision is needed for a generator I recently installed. I can probably provide one, but there's no factory provision for the connection, and it will probably void the Millbank warranty if I go splicing into the genny's control wiring to install an E-stop pushbutton.
For reference, I can yank the 20A 12V fuse that's part of the control circuit, and that will prevent the genny from starting, but that's "inside the generator enclosure," so I'm not sure it qualifies as a shutdown means.
Thoughts?
Thanks,
SceneryDriver