A question came to me regarding a generator problem in Afghanistan, I'm posting it here:
Greeting from Afghanistan. We are having a problem with our two 88KW generators. We run one generator at a time. About 6:00 pm each day it cuts out on us. The same thing happens with the other one. The voltage hold up pretty good. The current pull is about 100 amp on a 389 volt, 3 phase system. It should be able to handle around 133 amp. At one time we thought we had a balancing problem, now its balanced within 10 amps and we are still having the same problem. The altitude is about 6000 feet above sea level. We thought That maybe causing the problem, but it only happens for a few minutes then it recovers. If you have any thoughts on it I would appreciate your help.
Thanks
John
Greeting from Afghanistan. We are having a problem with our two 88KW generators. We run one generator at a time. About 6:00 pm each day it cuts out on us. The same thing happens with the other one. The voltage hold up pretty good. The current pull is about 100 amp on a 389 volt, 3 phase system. It should be able to handle around 133 amp. At one time we thought we had a balancing problem, now its balanced within 10 amps and we are still having the same problem. The altitude is about 6000 feet above sea level. We thought That maybe causing the problem, but it only happens for a few minutes then it recovers. If you have any thoughts on it I would appreciate your help.