Revision: 700.9(B) Wiring
The general requirements and concepts behind Section 700.9(B) relate to separation between emergency circuits from other than emergency loads, unless in accordance with the allowances provided in this section. Action by CMP-13 results in a new list Item (5) in Section 700.9(B). This additional text clarifies that the original separation requirements from the source to the loads, or from the source-distribution overcurrent protection to the loads, is to be required unless modified by any of the provisions in items (1) ? (5). The revised text will further clarify that it is permitted to supply any combination of emergency, legally required, or optional loads from a single feeder, or from multiple feeders, or from separate vertical sections of a switchboard that are supplied by either a common bus or individually. The use of an overcurrent protective device at the standby source or for the equipment is related to reliability and design. While the new requirements in (5)(b) maintain the highest degree of reliability, the exception to (5)(b) will also permit the use of an overcurrent device at the source or for the equipment. The coordination of the overcurrent protection at the source or for the equipment with the downstream overcurrent protection requirement in this exception will maintain the highest degree of reliability possible while allowing protection for conductors and equipment. The revised text in the main paragraph clarifies that circuits supplying emergency loads are not to be combined in panelboard enclosures with circuits supplying other loads (see figure 17).