Re: generator question SDS or Non-SDS
Originally posted by wirenut1980:Installer's preference?
I hope this doesn't offend the Installers on this Forum, but I would rather it be a ?Designer?s preference.? If the Installer is also doing the design, that is fine by me. But if one person (i.e., the Designer) made the choice, the Installer should not go the other way, without at least discussing it with the Designer. I know that many things I show on the drawings will not be installed in the exact manner that I designed. I know that panel schedules are high on the list of ?Designer?s Fiction.?
But I think the decision to use a 3-pole or a 4- pole ATS should be a design decision, and not a field decision.
That being said, I prefer to use a 4- pole ATS, and to make the generator the source of an SDS. I have no great reason and no really strong feelings on the topic, other than that it makes the relationship between the sources (i.e., separate and independent) easy to see. Also, there is no need to worry about removing the N-G bond that are installed by the generator manufacturers.