I am working on a building that has a 300 amp single phase service. After the meter the service is tapped in a trough with Polaris lugs going out to multiple panels. Directly after the meter, the neutral is bonded. Someone installed two separate backup generators on the building. I was called to figure out why lights keep burning out in building. I found that only flourescents with thermal overload ballasts were failing. When I opened the panels that were covered by backup generators, I found that the neutral bonds in those panels had been removed. I know this is standard procedure, but when you touch neutral to ground, it creates a humming sound. I found there to be no shorts in the building. When I went to the transfer switches, I found they had a neutral bonding jumper in each ATS. I am thinking this is a neutral problem. After looking up the specific models of generators, I found that the installation instructions show only one bonding jumper which should be in ATS. Finally, here is my question. Should I remove the bonding jumpers in the transfer switches or the bond after the meter? Or am I way off base? I appreciate any insight.
I read and re-read your description and to be honest I don't know for sure. ... While you may have some improper neutral bonding issues I can't see how that would make ballasts go bad.
I got to agree with Dave here. I'm not seeing the connection. So, is it the ballasts with the thermal overloads that are failing? The bulbs and non-thermally protected ballasts are working fine?
Qs:
Are the non-thermally protected ballasts running hotter than normal?
Are they connected to a different transformer?
Is the voltage different?
Are they drawing more/less current than comparable thermally protected ballasts?
Also agreeing with Dave, the plant has issues with Separately Derive Systems and NG bonding.
Do you have access to any one-lines? And I'm guessing no engineering staff?
Just curious:
Does the backup generation cover the whole plant or or just selected sections?
A 72KVA, single phase service (120/240?) is small. Definitely not industrial. Likely no motors other small (<5hp) HVAC
I'm guessing the generation is small, likely no more than 20kw - 50kw each.
Generally speaking, for every different configuration (generator\service line-up) there should be only one N-G bond. You will need to look at if the ATS are 2W or 3W (is the neutral switched). You will really need to put together a good one-line.
ice