I have several questions about a generator bid I I'm working on.
1. Does Kohler manufacture thier 60KW generators for Detroit Diesel or the other way around? If you go to their web sites and look at the pdf's of Kohler's 60RZG series and Detroit Diesels 60GSG Series you will see that they are identical except for brand designations. Same with thier transfer switches.
2. Because of engineering specs the generator is 1100 ft from the home. They also spec three parallel sets of 400mcm copper in 3in conduit to compensate for voltage drop. (I haven't verified the wire size with my own calculations yet). Does anyone have suggestions on how to install the wires. I think that by using two hand holes I can keep the pulls to 400 ft per segment.
3. What kind of pulling equipment would work the best. I'm looking at the Greenlee ultra tugger. It has 8000 lbs of pulling power. This is probably the only time I will ever need to pull such a long run of large cables.
4. What is the best source to get the generator from?
1. Does Kohler manufacture thier 60KW generators for Detroit Diesel or the other way around? If you go to their web sites and look at the pdf's of Kohler's 60RZG series and Detroit Diesels 60GSG Series you will see that they are identical except for brand designations. Same with thier transfer switches.
2. Because of engineering specs the generator is 1100 ft from the home. They also spec three parallel sets of 400mcm copper in 3in conduit to compensate for voltage drop. (I haven't verified the wire size with my own calculations yet). Does anyone have suggestions on how to install the wires. I think that by using two hand holes I can keep the pulls to 400 ft per segment.
3. What kind of pulling equipment would work the best. I'm looking at the Greenlee ultra tugger. It has 8000 lbs of pulling power. This is probably the only time I will ever need to pull such a long run of large cables.
4. What is the best source to get the generator from?