westelectric said:
ATS not switching neutral than no ground rod required. Is this typical. What about disco outside the gen?
Transfer switch does not transfer/switch the neutral which means it's not a SDS and the neutral must be isolated from ground inside the generator, but how does this impact the ground rod situation ? . 250.50 establishes the ground rod [or other electrode] requirement. . "structure served" must have an electrode. . It has nothing to do with the ATS or if the gen is categorized as a SDS.
I agree that "structure served" is somewhat ambiguous.
"What about disco outside the gen?"
Doesn't the generator have a breaker on it ? . This would be the disconnect and also wouldn't the existance of a disconnect on the gen push it toward being a "structure served".
Compare this to a pool.
Example #1, aboveground pool and motor is plugged into a one gang weatherproof box mounted to a pipe or peice of strut sticking out of the ground. . Ground rod at the plug box required ? . Most people would say it's not a "structure served".
Example #2, inground pool and motor is powered from a freestanding pedastal mounted subpanel that contains a couple of breakers. . Ground rod at the subpanel pedestal required ? . Many people would say it is a "structure served".
So is the generator, that has a breaker in it, like the pedestal subpanel. . They're both feed with a feeder. . Aren't they both a "structure served" ?
I have an even better question.
Why does 250.50 say "structure
served" and not "structure
supplied" ? . Does served mean a service ? . Does 250.50 apply to a second building supplied by a feeder from a first building ? . Or does the electrode requirement for the second building
only come from the wording found in 250.32 ? . The second building does
not have to be considered to be a "structure served" in order for 250.32 to apply.
Is there any ROP, ROC wording that addresses "structure served" for a building that is supplied by a feeder or branch circuit(s) ?