In NEC section 445.13
"The ampacity of the conductors from the generator terminals to the first distribution device(s) containing overcurrent protection shall not be less than 115 percent of the nameplate current rating of the generator."
What is considered a distribution device?
Take a 120/208 3 PH generator, that has an 175A main breaker as part of the generator. Is this main breaker considered a distrubution device or is the panelboard that it feeds via the ATS?