Got a customer who does wood working, and has purchased some 480V/3 equipment.
20HP Planer, 15HP Edger, etc....I figure he needs less than 100A to run what he wants.
The service into his building is 240V/1/60, and 3 phase is not available anywhere near his site (5 miles away).
He's also got a 350KVA 480V diesel generator that he wants to use to power this equipment.
This (used) generator has a 100A 3 pole fusible disconnect mounted on it's exterior that's apparently been used in the past as the disconnect for this generator. The conductors from the generator terminals to this disconnect are #2cu.
This seems to be a violation of 445.13.
I understand that the conductors from the generator output to the first overcurrent device must be sized for 115% of the generator capacity.
In this case 500A...correct?
Does this mean that the generator disconnect has to be rated for 500A?
That may be a stupid question
My mind says yes, but I'm having a problem understanding the reason.
All I need is 100A from this generator.
Can I not just fuse my feeder from this generator at 100A to power a 100A MLO panel inside the building?
If I have to set a 500A disconnect at the generator and feed it with 500A cable, can I then use the 10' tap rule to power a 100A Main breaker panel from this 500A disco?
I tried to sell this guy on using inverters to get 3 phase power for this equipment, but he's not interested.
This guy is a multi-millionaire that made his money building, owning and operating large equipment, and this wood working is just a hobby..albeit a large one.
He's quite a character.
He wants to use this generator, and this 3 phase equipment.
What would you do?
Any ideas are appreciated.
steve
20HP Planer, 15HP Edger, etc....I figure he needs less than 100A to run what he wants.
The service into his building is 240V/1/60, and 3 phase is not available anywhere near his site (5 miles away).
He's also got a 350KVA 480V diesel generator that he wants to use to power this equipment.
This (used) generator has a 100A 3 pole fusible disconnect mounted on it's exterior that's apparently been used in the past as the disconnect for this generator. The conductors from the generator terminals to this disconnect are #2cu.
This seems to be a violation of 445.13.
I understand that the conductors from the generator output to the first overcurrent device must be sized for 115% of the generator capacity.
In this case 500A...correct?
Does this mean that the generator disconnect has to be rated for 500A?
That may be a stupid question
My mind says yes, but I'm having a problem understanding the reason.
All I need is 100A from this generator.
Can I not just fuse my feeder from this generator at 100A to power a 100A MLO panel inside the building?
If I have to set a 500A disconnect at the generator and feed it with 500A cable, can I then use the 10' tap rule to power a 100A Main breaker panel from this 500A disco?
I tried to sell this guy on using inverters to get 3 phase power for this equipment, but he's not interested.
This guy is a multi-millionaire that made his money building, owning and operating large equipment, and this wood working is just a hobby..albeit a large one.
He wants to use this generator, and this 3 phase equipment.
What would you do?
Any ideas are appreciated.
steve