I went to a job site and found a standby generator name plate reads 2000KW & 13200V. However, the building utility is served from 12.47KV. (Q1) is it possible to adjust the voltage system on the generator to deliver 12.47KV? (Q2)Is there any reason why they didn't purchase generator rated for 12.47KV to start with? ...
Q2: Generally it is about the money. And specifically it is about the money.:roll:
Look at the dates the equipment was purchased.
Modern distribution will be 13.8 KV - that matches with 480V. Older systems, say 1960s and older will be 13.2KV - that matches with 440V.
12.47 is a bit odd any more. Anecdotal information (no reference) suggests it was driven by REA. 12.46kv/7200V was compatible with the single phase rural services.
Q1: Sure. Have to watch low end leading vars, minimum excitation level, stability, power output will not make nameplate. Might take an exciter change - might not.
ice