Generator Rating Question

Status
Not open for further replies.

Sajid khan

Senior Member
Location
Pakistan
Why the bigger generators are rated in kW instead of KVA rating. E.g i have seen 2500kW rating for both gas gensets and diesel gensets.

If some one can explain please..

Thanks

Sent from my GT-I9300I using Tapatalk
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Why the bigger generators are rated in kW instead of KVA rating. E.g i have seen 2500kW rating for both gas gensets and diesel gensets.

If some one can explain please..

Thanks

Sent from my GT-I9300I using Tapatalk


Most generators I have seen large and small are rated in both KVA and KW.
 

ron

Senior Member
All generators are rated in both kW and kVA.

Sometimes depending on the load, one will be more of a critical threshold than the other. Whichever you hit first is the limit.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Why the bigger generators are rated in kW instead of KVA rating. E.g i have seen 2500kW rating for both gas gensets and diesel gensets.

If some one can explain please..

Thanks

Sent from my GT-I9300I using Tapatalk

As already mentioned, the genset will have both a KW and KVA rating. The KVA rating will tell you how much current it can handle. The KW rating tells you how much power it will deliver. With a genset this is critical info as the KVA relates to the generator current capacity and the prime mover relates to the power it can deliver (KW). As an extreme example, a genset rated 100 KVA @ .5 PF will only have enough engine to provide 50 KW.
 

JoeStillman

Senior Member
Location
West Chester, PA
I like to think of it like this; kW is the rating of the engine, kVA is the rating of the alternator.

Because the kW rating is typically 80% of the kVA, it means the engine can't produce enough energy to overload the alternator as long as the load power factor is above 80%.
 

publicgood

Senior Member
Location
WI, USA
Standard application is based on 0.8 PF. If the actual PF is higher, you may get more out of the generator, which is why you must size this way. We don’t typically design beyond the rating for capacity...so using kW. This also helps concerns for elevation derates if they apply as conservative.
 