The job has a detached generator as an option power system. The transfer switch does switch the neutral.
The disconnect on the generator is not service rated.
A system bonding jumper sized per 250.66 is installed between the generator grounded conductor and the frame and two ground rods are also connected to the grounded conductor at the generator.
From the generator the phase conductors and ground conductor are routed to a service rated disconnect at the premises.
An equipment grounding conductor based on the generator OCP is routed with the supply conductors and is bonded to the premises disconnect.
In addition a connection is made from this EGC to the premises grounding electrode system. No connection is made between the grounded conductor and grounding conductor at the premises.
Doe this sound correct ?
The disconnect on the generator is not service rated.
A system bonding jumper sized per 250.66 is installed between the generator grounded conductor and the frame and two ground rods are also connected to the grounded conductor at the generator.
From the generator the phase conductors and ground conductor are routed to a service rated disconnect at the premises.
An equipment grounding conductor based on the generator OCP is routed with the supply conductors and is bonded to the premises disconnect.
In addition a connection is made from this EGC to the premises grounding electrode system. No connection is made between the grounded conductor and grounding conductor at the premises.
Doe this sound correct ?