codequestion
Banned
- Location
- MD, USA
Is the following grounding and bonding shown for the generator okay for non separately derived system? Is it per NEC 2014 Article 250.30?
The drawing at first glace looks correct to me for a non-SDS. Why are you asking about 250.30? That is for SDS.
Also, while allowed, the GES shown for the genset is not required for a non-SDS install such as this.
The pdf shows generator has grounding electrode and the generator is non separately derived. NEC 2014 exhibit 250.12 does not generator having any grounding electrode. Should not the grounding electrodes be removed at the generator? Thus main reason for asking.
So why does not nec 2014 exhbit recommend this? And whats the purpose of grounding electrode?Yes it does show a grounding electrode at the generator, however, it does not show the Neutral bonded to the grounding electrode at the generator.
JAP>
The pdf shows generator has grounding electrode and the generator is non separately derived. NEC 2014 exhibit 250.12 does not generator having any grounding electrode. Should not the grounding electrodes be removed at the generator? Thus main reason for asking.