165kvawhat is the calculation: 2no 22KW water pumps how much KVA the gen set required.
If the pump motor is rated in kW, that's usually output kW, so it can be directly converted to HP... then 430 Tables come into play for determining kVA.I am not sure I understand the question, but I don't think Iceworm's answer is right. Are you saying you have two water pumps, and that each draws 22 kw? So you have a total of 44 kw. All you need to know is the power factor of each pump's motor. Not knowing anything else, I would assign a power factor of 0.8. That will give you a KVA value of (44 / 0.8) or 55 KVA, just for the two pumps. But you didn't say whether any other load would be powered from the same generator. So the total KVA cannot be determined from the information you did give.
Or more than just largest motor if you expect all of them to try to start the moment the genny comes online.If the pump motor is rated in kW, that's usually output kW, so it can be directly converted to HP... then 430 Tables come into play for determining kVA.
And don't forget 125% factoring for largest motor.
what is the calculation: 2no 22KW water pumps how much KVA the gen set required. ...
165kva
I am not sure I understand the question, but I don't think Iceworm's answer is right. ...
... So the total KVA cannot be determined from the information you did give.