Good day,
I have an issue on which I would appreciate input: We generate our own electricity with five 1.6MW sets usually running (No connection to the grid). Each genset has a Cummins Powercontrol 3201 operator panel. The main control signal is common to all - each set does not have it's own individual kilowatt target.
We installed a newly serviced (half-life service) Cummins engine on one of the gensets. When running it, the set synchronizes and the engine runs fine with the voltages and frequency on target. As soon as the breaker is closed, the current ramps up and continues to do so for four to six seconds, right up to and over the rated value at which point the the protection circuit switches the breaker out.
Most of the cards were installed new with the exception of the base card.
Any input would be appreciated, thank you in advance.
Caleb
I have an issue on which I would appreciate input: We generate our own electricity with five 1.6MW sets usually running (No connection to the grid). Each genset has a Cummins Powercontrol 3201 operator panel. The main control signal is common to all - each set does not have it's own individual kilowatt target.
We installed a newly serviced (half-life service) Cummins engine on one of the gensets. When running it, the set synchronizes and the engine runs fine with the voltages and frequency on target. As soon as the breaker is closed, the current ramps up and continues to do so for four to six seconds, right up to and over the rated value at which point the the protection circuit switches the breaker out.
Most of the cards were installed new with the exception of the base card.
Any input would be appreciated, thank you in advance.
Caleb