thakerrohit -
Dan is absolutely right - get the data from the nameplate.
As for the calcs working in the field, generator manufacturers don't tend to lie about ratings on industrial generators. However, they do rate their generators at the most favorable ambient conditions. So, if your installation is limited on cooling, altitude, or has air intake restrictions or high ambient temperatures, then the gen likely will not make rated output.
A couple of questions:
1) How do you know the customer's load is bordering on the gen KVAR limits? Is this something measured on an existing installation? Or is this calculated for a new installation?
2) What test are you thinking of performing? Is this a new installation and you want to make sure the gens will output as specified? Are you considering getting a loadbank with a variable pf?
More information about the installation will likely get better answers.
Dan is right about the required instrumentation - you need it. I would be surprised if it is not there. Every paralleled gen installation I've seen has the needed instrumentation.
carl